External i/o connector

Posted: Wed Jun 21, 2006 3:34 pm
by jharris
Hi Hope you can help!

I need more info on the external I/O port. Im using a PLC running relays to switch between scenes. It works fine when only 1 port is triggered. However when you trigger multiple ports, to get a binary number, the unit gets confused. Im sending a 5 second long burst of the correct port address.
How does the SLESA know when multiple ports are connected not to look at them as indvidual triggers? What happens with switch bounce? How close must mutiple port addresses arrive together to be counted as one binary number.

Best regards
Jon Harris

Yes!

Posted: Mon Jan 01, 2007 4:28 pm
by adam1976
I couldnt ask that question any better. Any help on this will be a big help. We are having the same problem!!!.

Posted: Tue Jan 02, 2007 8:44 am
by julien
Hi
The processor checks every 80ms the state of the I/O port.
You don't need a burst.